  • 1.  Heat output from EX switches

     
    Posted 08-03-2017 02:53

    Does anyone know what the heat output is for the EX3400 & EX2200-C? I can not find this information anywhere.



  • 2.  RE: Heat output from EX switches
    Best Answer

    Posted 08-03-2017 02:59

    I assume you are trying to measure an AC load.  If so, you can use the equipment watts rating and convert to BTU load using the standard formula

    BTU load=3.412141633xWatts

     

    http://www.rapidtables.com/convert/power/Watt_to_BTU.htm



  • 3.  RE: Heat output from EX switches

    Posted 08-03-2017 04:33

    Hi Regalis,

     

     

    usually your local Juniper Partner should be able to get hold of this information. There is a document provided to Juniper and Partner SE's with precise numbers for wiring closet switches with different traffic and PoE load.

     

     

    I'm not allowed to give out these numbers in a public forum - so you need to go via your local partner.

     

    -- 

    Best regards,

     

    Jonas Hauge


    #powerconsumption
    #EX
    #BTU
    #heat